Posted by ED C on Sunday, 4 May 2008, at 5:50 p.m.
regarding the coldflowac heat pump here is the end (i hope) of the story:
unit was not low on freon, added per factory instructions, both suction & head pressures increased 'til finally kinked off on high press.
factory agreed to take unit back & repair which is not their normal policy; they were very nice to deal with but so busy- hard to contact.
unit returned three months later (4-21-08). alas it was a little worse than before:86psi suction, 152psi head. contacted factory again & after only two phone calls they said to ship back at their expense for a refund (from buyunit.com-company bought from.)
did notice unit had a 3&1/2 to 5 ton txv instead of a two ton. this would explain a lot but factory tech said that's how they build them.
also had an 18,000btu copeland scroll instead of a 24,000 as it is rated, which may not matter.
overall quality of the COLDFLOWAC appeared very good: copeland scroll,parker-hannifin txv, stainless steel cabinet, easily maintainable controls.
i really wanted this to work & invested approx $700 in setup & diagnostic equipment. may go to gas furnace & build my own grd water h. pump.