Introduction
  The House
  >> Live data
  >> Trend data
  >> Efficiency

  WEL
  >> (Web Energy Logger)
  >> (WEL World map)

  The Land
  Wildlife
  About Us
  Talk/Forum
  >> Archives

  Podcast Info
  Links (Resources)
  Books

Construction Pics
  Foundation
  Radiant Slab
  Acid Stain floors
  Ground Loop
  Wood Framing
  Mechanical
  Equipment Room
  Monitoring System
  Exterior
  Interior
Mission Statement
  Earth (Sheltering)
  Sun (Passive Solar)
  Water (Geothermal)    >> Efficiency test
Design Process
  Timeline
  Goals
  Room Guide
  Concepts
  Preliminary
  3D Model
  Final Design
  Download Plan
Energy Mgmt.
  GREEN HVAC
  Energy Logger
  The Weather
Related Stuff
  Designer Showcase
  >> Brian
  >> Scott Hall
  >> Jeff Ray
  Discussion Forum
  Web-Cam
  Marsupials
Keyword Search:
 
Phil's Other Stuff
  GEARS
  SUGO
  FIRST Team 1629
  Resume
Jazzercise
  Chatter
  MegaTalk
  Chatter2
  Chatter3


Re: Loss of temp sensors due lighting.

[ Read Responses | Return to the Index ]
[ ]

Posted by Phil on Saturday, 4 July 2009, at 10:07 a.m.,
in response to Re: Loss of temp sensors due lighting., posted by Bob

Sorry for the lack of response... it's been a busy week for me, I'm running an Underwater Robotiocs camp for Middle Schoolers....

OK.

First thing to note about the WEL vs a PC based monitoring system:

All Desktop PCs have their 0V supplies connected to chassis ground (electrical earth), so if an attached signal cable is raised to a high potential, there is a current path to ground, so part of any protection system is series-resistors to limit the current flow, and any high voltage protection needs to be referenced to chassis ground. This is what all the comments that refer to the DS9097U are about.... the DS9097U ties the 1-wire bus ground to chassis ground and thereby to mains earth. It needs special protection.

The WEL doesn't have this problem, because it's 0V is not connected to Earth or any external potential (the plug pack is isolated through the transformer, and the Ethernet is isolated through transformers.) The only possible ground is if you use the serial port to talk to your computer). So you can ignore any references to schemes to protect the DS9097U.

The second thing to know is that the WEL already uses a bidirectional Zenner protection device to kill high voltage surges. I use the P6KE7V5CA which has a 7.5 V threshold and a 600W rating. I used to use the 1.5KW rating device but it became un-available.

This device it located right at the output terminals on the WEL board and has large traces to protect the board.

The problem is that the individual sensors don't have surge supression. If you take great pains to protect the WEL (by installing in-line resistors) the sensors are left high and dry.

Since you may have many feet of wiring, even if you snub the voltage at the WEL, sensors at the other end of a line are left somewhat unprotected.

My only thought was to put the surge supressors at the end of each bus run to snub voltages at both ends.

The other thing to note is that twisted pair wire also minimized the amount of differential voltage induced by lightning. If you have any stretches of bus wiring that uses non-twisted cable (like thermostat wire) then you will be more prone to differential voltages.

As for the Thermostat Monitor board being a some form of factor... I'm not sure why this would be the case. The thermostat inputs might get induced spikes on them, but they are optically isolated from the WEL bus. Plus, this board ALSO has a transient protector on it, so it's actually boosting the protection on the bus.

Perhaps the thing to be drawn from the way the sensors failed here is that the Thermostat board was actually acting as an end-of-the-line snubber for the "inside" portion of the bus. That portion that was "beyond" the thermostat board was only snubbed at one end, so it was more suceptable. Another argument for placing snubbers at the end of the bus.

I will try adding P6KE7V5CA devies along my bus to see if they degrade performance in any way.


Responses


© 2000-2010, Phil and Lisa's relaxed lifestyle home.
An exercise in Energy Smart, Not So Big living.
www.OurCoolHouse.com - Ideas@OurCoolHouse.com
Google
 
Web OurCoolHouse.com

This site is all about building a cool, energy efficient house, that makes maximum use of earth sheltered design, passive solar heating and cooling, geothermal exchange energy management, and right sizing of the house for it's designated use. The home's placement is on a south-facing hillside in Deep Creek Lake, Maryland. This site describes the design process, the technologies used and the expected results. We also have a comprehensive Links Page for anyone who is also interested in designing a similar project.